    came across this on Reddit of a condo owner who has an outdoor 14-50 outlet and plugs his UMC into it every 2-3 days over the last two years.
    tl:dr the outlet he was using was not designed for repetitive plugging and unplugging and wear caused the prongs to no longer making solid contact inside the outlet, causing excess heat at the bad connection.
    If you are planning something similar, make sure you are installing a receptacle intended to have daily use and not a typical appliance outlet that is rarely unplugged, and replace if the socket begins to feel loose when plugging into it.

     
    • Informative Informative x 8
    • Agree Agree x 1
  2. Uricasha

    Well-Known Member
    Expand Collapse

    Joined:
    Feb 19, 2017
    Messages:
    219
    Location:
    Phoenix, AZ
    Tesla Owner:
    No
    Country:
    Country
    Could be the recalled connector?
     
  3. MelindaV

    ☰ > 3
    Moderator
    Expand Collapse

    Joined:
    Apr 2, 2016
    Messages:
    5,015
    Location:
    Vancouver, WA
    Tesla Owner:
    Reservation
    Country:
    Country
    No, it was the standard 14-50 and issue originated in the outlet, not the plug.
     
    • Informative Informative x 1
  4. JWardell

    Top-Contributor
    Expand Collapse

    Joined:
    May 9, 2016
    Messages:
    1,583
    Location:
    Boston
    Tesla Owner:
    Reservation
    Country:
    Country
    I saw this on Reddit, too. It was simply caused by extreme heat due to a bad or loose connection in the plug or socket. It could be very dirty prongs, or a very loose wire connection inside the socket. No part of the charger or cable failed here, and it's easy to repair/replace.
    I really doubt that it was due to the socket not being designed for repetitive connection. It's no different, and better off, than any other socket. It's very likely that the prong was dirty or corroded.
    This does illustrate an issue I often seen with regular plugs at home, though. Home depot usually has "value" and "premium" options on the shelf for each kind of outlet. The premium versions have much beefier contacts in the sockets as well as higher general build quality. The budget sockets will have problems like this within a few years of use. Go for the premium when you have the option.
     
    • Informative Informative x 3
  5. RandyS

    Active Member
    Expand Collapse

    Joined:
    Apr 6, 2016
    Messages:
    142
    Location:
    San Diego
    My two cents worth....

    * For a better connection, orient the receptacle so the plug and cable to the UMC point down (not sticking up and then looping down)
    * Install some sort of strain relief for the UMC brick so it doesn't put weight on the connection and start to pull it out of the receptacle
    * Inspect the connections, cords, plugs, etc. occasionally to make sure everything is okay
    * Think about getting a HPWC (Which doesn't have these connection problems) and leave the UMC in the trunk for occasional use...
     
    • Like Like x 1
    • Informative Informative x 1
  6. SoFlaModel3

    Team Midnight Silver
    Moderator M3OC Supporting Member
    Expand Collapse

    Joined:
    Apr 15, 2017
    Messages:
    7,189
    Location:
    Florida
    Tesla Owner:
    Model 3
    Country:
    Country
    I am comfortable with electrical work, but certainly no electrician. I have always scratched my head at why my dryer plugs in upside down. I certainly will make note of that when I get one installed in my garage... unless of course I get the Tesla wall charger.
     
  7. garsh

    Dis Member
    Moderator M3OC Supporting Member
    Expand Collapse

    Joined:
    Apr 4, 2016
    Messages:
    5,553
    Location:
    Pittsburgh PA
    Country:
    Country
    Which way is that? I don't have a UMC yet.
     
  8. MelindaV

    ☰ > 3
    Moderator
    Expand Collapse

    Joined:
    Apr 2, 2016
    Messages:
    5,015
    Location:
    Vancouver, WA
    Tesla Owner:
    Reservation
    Country:
    Country
    this is the correct orientation with the pin on the top
    [​IMG]
    [​IMG]
     
    • Informative Informative x 4
  9. 17.088

    Active Member
    Expand Collapse

    Joined:
    Oct 15, 2016
    Messages:
    54
    Location:
    Twin Cities, Minnesota
    Country:
    Country
    Sorry to be nit-picky, but technically NO, the correct word is not "correct", it is "most relevant".
    The National Electrical Code (US-primarily, I know) does not specify which direction the ground prong must face.

    It's true that buildings East of the Appalachian mountains and Hospitals tend to have the ground up, but otherwise most of the U.S. tends to have the ground on the bottom side.

    In other words, do what is most relevant to your load's needs, whether that be a dryer plug or an EVSE plug.

    17.088 ^2
     
  10. SoFlaModel3

    Team Midnight Silver
    Moderator M3OC Supporting Member
    Expand Collapse

    Joined:
    Apr 15, 2017
    Messages:
    7,189
    Location:
    Florida
    Tesla Owner:
    Model 3
    Country:
    Country
    Tesla suggests ground up for the Nema 14-50.
     
    • Agree Agree x 1
  11. 17.088

    Active Member
    Expand Collapse

    Joined:
    Oct 15, 2016
    Messages:
    54
    Location:
    Twin Cities, Minnesota
    Country:
    Country
    And for a very good reason.
    Look at how their cord is manufactured; gravity is pulling down on the cord in such a way that the if the ground had been on the bottom, a lot of stress would be on the connection.
    The ground terminal on the top, given the design of their plug, makes the most sense.

    It's a classic situation of doing what makes sense as opposed to doing whatever you want to do.
    Or put another way, pay attention to the application, and let that drive your installation.
    In this case, having the ground up IS the most relevant thing to do.
    But STRICTLY speaking it's neither correct nor incorrect, just relevant.

    Yea, yea, a nitpick, I know.
     
    • Agree Agree x 1
  12. RunCycle

    Active Member
    Expand Collapse

    Joined:
    Jan 21, 2018
    Messages:
    194
    Location:
    California
    Tesla Owner:
    Model 3
    Country:
    Country
    I have a couple questions about outside charging.
    1. Is it better to keep the Mobile Charger plugged into the NEMA 14-50 socket all the time outside or to unplug it each time you charge?
    2. Would it be better to install a Tesla Wall Charger outside instead of the NEMA 14-50?
     
  13. SoFlaModel3

    Team Midnight Silver
    Moderator M3OC Supporting Member
    Expand Collapse

    Joined:
    Apr 15, 2017
    Messages:
    7,189
    Location:
    Florida
    Tesla Owner:
    Model 3
    Country:
    Country
    Technically speaking, I believe the UMC is rated for outdoor use so you should be fine. That said, if my setup was outside I probably would get the HPWC. It would feel safer to me and also not have the worry of someone stealing my UMC as I wouldn’t want to unplug/re-plug for every charge.
     
    • Agree Agree x 2
  14. M3OC Rules

    M3OC Supporting Member
    M3OC Supporting Member
    Expand Collapse

    Joined:
    Nov 17, 2016
    Messages:
    223
    Location:
    Minneapolis, MN
    Tesla Owner:
    Reservation
    Country:
    Country
    Not sure if this is going to happen but I was told Tesla is going to stop recommending NEMA 14-50 because of issues with some GFI breakers. California may not require GFI but you probably should have it for an outdoor outlet. You don't need GFI breakers if its hardwired, ie wall connector. With the Wall Connector you also don't have to worry about wearing out the socket by regular plugging or someone stealing your $300 cable. The Wall Connector can also provide faster charging if wired for it, can be daisy chained to allow multiple Wall Connectors to share one circuit, and provides diagnostics if something is wrong with the wiring. Also it looks cool and integrates a wall hanger for the cable. Only downsides are you can't plug in anything else there and cost.
     
    • Agree Agree x 1
    • Informative Informative x 1
  15. oey192

    Active Member
    Expand Collapse

    Joined:
    Aug 31, 2017
    Messages:
    84
    Location:
    Seattle, WA
    Tesla Owner:
    Model 3
    Country:
    Country
    I have talked to two different Tesla employees in a showroom (once in Jul 2017, once in Jan 2018) and both times they recommended the 14-50 plug with UMC over a HPWC. I ignored their advice and am having a HPWC installed when my solar system goes up (next week!) because I don’t want to have to worry about the UMC getting warm when plugged into the wall but not the car and because I think I will want to daisy chain a second HPWC on the same circuit in a few years when the Model Y comes out and my house gets its second Tesla…
    My electric panel also has enough capacity for the HPWC to get 60A so I can charge my LR (AWD) Model 3 at its max speed for the very rare cases I will need to do so.

    My setup is indoors but outdoors I would definitely get an HPWC over a 14-50 outlet even without the other considerations above.

    Also, since AWD is still a ways off I got a UMC to J1772 adapter so I can charge my Leaf with the HPWC until my Model 3 arrives (right now I trickle charge the Leaf). This somewhat negates the downside of not being able to plug anything else into the 14-50 outlet, especially since the pre-2018 Leaf EVSE doesn’t work with a 14-50 outlet out of the box.
     
    • Like Like x 2
    • Agree Agree x 2
  16. RunCycle

    Active Member
    Expand Collapse

    Joined:
    Jan 21, 2018
    Messages:
    194
    Location:
    California
    Tesla Owner:
    Model 3
    Country:
    Country
    Thanks for your replies. We are thinking of getting a padlock and locking the Mobile Connector cord to the house or fence or something even though it won't be visible from the street when not in use.
     
  17. Vin

    Vin
    Active Member
    Expand Collapse

    Joined:
    Mar 30, 2017
    Messages:
    158
    Location:
    Philadelphia, PA
    Country:
    Country
    #17 Vin, Mar 8, 2018
    Last edited: Mar 8, 2018
    I was curious as to the thickness/diameter of the HWPC vs. the UMC cables because I'm getting a cable cover (similar to what they use for outdoor concerts) to protect the cable across a sidewalk when plugged in (once or twice a week).
    Does anyone who owns both notice a big difference or is it basically minor?

    Thanks.
     
  18. garsh

    Dis Member
    Moderator M3OC Supporting Member
    Expand Collapse

    Joined:
    Apr 4, 2016
    Messages:
    5,553
    Location:
    Pittsburgh PA
    Country:
    Country
    • Funny Funny x 1
  19. Vin

    Vin
    Active Member
    Expand Collapse

    Joined:
    Mar 30, 2017
    Messages:
    158
    Location:
    Philadelphia, PA
    Country:
    Country
    Good call, lol. I meant cables, thx :) I corrected my post master obiwan
     
    • Funny Funny x 1
  20. theishu

    Dream Car Unlocked
    Expand Collapse

    Joined:
    Mar 21, 2017
    Messages:
    143
    Location:
    Fairfax, VA
    Tesla Owner:
    Model 3
    Country:
    Country
    Ditto!
     

Share This Page

Model 3 Owners Club © 2018. All rights reserved.
Model 3 Owners Club (M3OC) is an enthusiast club and is not affiliated with Tesla Motors or the Tesla Motors Club Forum (TMC).
All Tesla logos are trademarks or registered trademarks of Tesla Motors.